A: How do I properly ground my subpanel that only has one neutral/ground bar?

TimChanges to the Electrical Code now REQUIRE all unattached buildings with sub panels, to have the Neutral Bar Grounded with #6 wire to the panel box then to a grounding rod in the earth. (Rule 10-208) You CANNOT use the ground included in say #10/3 wire as your sub panel ground anymore. You are...

 
2:15 PM
Done my twenty for the day. A little help here?
 
2:36 PM
@ChrisCudmore I don't know what code they are referencing.
I also think they might be confusing the grounded "neutral" bar with the grounding bar.
CEC 10-208 "Where two or more buildings are supplied from a single service:
a) The grounded circuit conductor at each building shall be connected to a grounding electrode and boded to the non current carrying parts of electrical equipment"
From here
I can't find the actual code, so I have no idea what else it says.
Don't know what exceptions, or other articles apply.
From what I can find, it appears that they require the grounded "neural" conductor of the feeder to be bonded to the grounding electrode in the second structure, if the building was supplied by a 3 wire feeder ("hot", "hot", "neutral"). However, if the building is supplied with a 4 wire feeder (and does not contain livestock), the "neutral" should not be bonded.
Seems similar to NEC, except that NEC now requires a 4 wire feeder.
 